> Extreme Boondocking, Heating
pianotuna
post Aug 10 2009, 06:49 PM
Post #1


Advanced Member
******

Group: Members
Posts: 1031
Joined: 7-January 07
Member No.: 10403



Hi all,

My RV is Kustom Koach based on the Ford E-450 chassis. It is equipped with a "Dometic" Briskaire Roof Ducted Air Conditioner c/w Heat Strip, and a "Hydroflame" DSI Furnace.

I want to be able to use the heat strip and the furnace at the same time--however both are controlled by one thermostat on the wall--and it is not possible to have the switch in two positions at once.

Does anyone have a "work around" for this situation? (I'd not object to adding a 2nd thermostat if that is what it takes.


--------------------
Regards,

Don
User is offlineProfile CardPM
Go to the top of the page
+Quote Post
Trentheim
post Aug 10 2009, 07:28 PM
Post #2


Advanced Member
******

Group: Members
Posts: 83
Joined: 13-November 07
Member No.: 17858



I gotta ask what you are needing to do that requires both at the same time. You got me perplexed. (You're not stress testing your solar panel solutions are you?)

I think you can use one thermostat, but I would suggest two just to keep better control over the temperatures of the system.


--------------------
If you can't fix it with a hammer, you've got an electrical problem.
User is offlineProfile CardPM
Go to the top of the page
+Quote Post
pianotuna
post Aug 10 2009, 07:56 PM
Post #3


Advanced Member
******

Group: Members
Posts: 1031
Joined: 7-January 07
Member No.: 10403



Hi Trentham,

I can't use one thermostat because the selection setting switch is furnace, airconditioner, off, and heat strip. It can't be in two positions at once.

I want to be able to use both to increase the speed at which I can warm up the RV--and also to have the heat strip carry as much of the load as possible--setting the furnace to cut in a degree or two colder than the heat strip setting.


--------------------
Regards,

Don
User is offlineProfile CardPM
Go to the top of the page
+Quote Post
gsbogart
post Aug 12 2009, 09:52 AM
Post #4


Advanced Member
******

Group: Members
Posts: 79
Joined: 10-January 06
Member No.: 5114



QUOTE(pianotuna @ Aug 10 2009, 09:56 PM) *

Hi Trentham,

I can't use one thermostat because the selection setting switch is furnace, airconditioner, off, and heat strip. It can't be in two positions at once.

I want to be able to use both to increase the speed at which I can warm up the RV--and also to have the heat strip carry as much of the load as possible--setting the furnace to cut in a degree or two colder than the heat strip setting.


Don
I think you answered your own question when you said you wanted the heat strip to carry a load different from the furnace.
The only way you can do that is with two thermostats. However, if you are looking for a 2 stage system, that is possible with a 2 stage heat cool thermostat, but you might need to run some additional wiring depending on what is in the back of the existing thermostat hookup. Most heat pump thermostats are 2 stage heat, one stage cool, and are available from home depot.
Run the w1 terminal to the furnace along with a ground wire. Run W2 to the heat strip contactor, and the y1 to the cooling contactor on the A/C. Run the G to the fan contactor. The R terminal is for the transformer or control voltage input.
You will not need the Orange or blue which go to the reversing valve in two types of wiring scenarios.
User is offlineProfile CardPM
Go to the top of the page
+Quote Post